Mixing valves, Controls, multi-zone radiant
Ed_26
Member Posts: 284
Mike, pg. 17/18 shows condensate piping etc.
For the multi-zone radiant - a mixing block w/controls?
Mixing valves, Controls, Radiant
A number 356 Controler along with "mixing valves and a variable speed injector pump was recommended on a previous thread for three 200 sq ft rooms. according to the company tech sheet the 356 controler seems to be for a "NON-condensing boiler". However the heat source is an A.O. Smith vertex "Condensing" hot water heater (90% efficient).
My question is what mechanical layout would I need to "mix" water at 160 degrees F to the 1/2" pex room, while mixing 110 to 120 degree F to the other two 5/8" pex rooms? All fed from the vertex heater. No potable domestic hot water involved. I do not know if you can even interface any "control" device to the vertex heater.0 -
Unless I missed something the A.O. Smith has no drain for condensate. If there's no provision to drain the condensate it is NOT a condensing appliance regardless of any efficiency rating.0 -
356
The Tekmar 356 controller will work for a condensing or non condensing boiler. If you use one of these controls you would run your boiler at 160 degrees and you would mix down a lower temp circut to the 110 to 120 desired temp. Another option would be to use a Taco RMB. It would accomplish the mixing and could be setup to do outdoor reset on your lower temp loop increasing comfort and operating efficiency.0
- 86.7K THE MAIN WALL
- 55 Biomass
- 102 Chimneys & Flues
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 43 Industry Classes
