Domestic hot water recirculation problem
Tim_59
Member Posts: 9
I use a grunfos uP15 with a timer. I run my hot water at 140F. I mix it to 120 and all is well except when the recirc pump runs. The temp goes to 140F in the line until a faucet is cracked and then the cold water tempers it.
I have tried aquastats and they still do not help the problem. Has anyone else run into this situation and cured it? I think if I used the grunfos up10 with an integral adjustable aquasta it would help but not cure the problem. I have noticed Armstrong make units with digital controls.
Has anyone used the Armstrong controls?
Tim
I have tried aquastats and they still do not help the problem. Has anyone else run into this situation and cured it? I think if I used the grunfos up10 with an integral adjustable aquasta it would help but not cure the problem. I have noticed Armstrong make units with digital controls.
Has anyone used the Armstrong controls?
Tim
0
Comments
-
Maybe your recirc line is not tied in correctly ! Some pix/Drawings may help ! BTW honeywell Braukmann makes a Antiscald valve that has the recirc port build into the valve! that should make the install easy'r. Richard from Heatmeister.0 -
Some pictures
I will look into the new valve.
Tim0 -
Pump Direction
Any chance your check valve and pump are backwards and you are drawing water from the bottom of the tank instead of pumping into the bottom of the tank and drawing through the mixing valve?0 -
I think that scenario would give me cool water in the line.
The pumps is flowing correctly and the check valve is in the correct orientation. I had the check valve above the mixing valve with the same results. I may move it back above the valve, Sparco diagram shows it that way.
Tim0 -
You have to return water.....
..... back to the tank and the cold side of the mixing valve.0 -
Watts mixing valve
Tim, I was having the same type of problem. Hot water from the tank would back feed into the cold and whenever I opened a hot water faucet I would get a good dose of scalding hot water. The mixing valve I had did not have any checks in it. I bought a watts valve that has 2 checks built in and it did the trick....0 -
Watts
Thank You.Do you know the part number?
Tim0 -
Mixing Valve
Series MMV-M1 is the one I have.0 -
Here is a quote from watts antiscald valve guide . I think I need to use an adjustable aquastat. I used a fixed taco unit. I don't think it is sensitive enough for this application.
"Aquastat - An Aquastat must be used to control the on/off
operation of the circulator. The Aquastat is set 5°F to 10°F lower
than the mixed water outlet temperature of the tempering valve.
The circulator cannot be allowed to run continuously because
bypass through the mixing valve will eventually allow the temperature
in the piping to climb to that of the hot water heater during
no draw periods."
Tim0 -
Overkill
Electronic adjustable aquastat from Johnson Controls.
http://www.houseneeds.com/shop/manuals/johnsoncontrol_a419bulletin.pdf0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements