1-pipe line blockage
Daniel_3
Daniel_3 Member Posts: 543
Possibly a sagging horizontal feed instead of blockage. If it is, the hose will do you no good. Examine all the pipes first for porper pitch.
  • 1-pipe line blockage
    i have one radiator fed by a 20 ft.x 11/4 riser which has a couple of short horizontals sections of pipe in it.the riser bangs so i think there is a partial blockage preventing the pipe from draining.
    do you think i could attach a hose to the air vent tapping and flush the riser out with gentle hose pressure? one horizontal section is under the floor and the other is in the basement , so this is an alternative to cutting into the section i can get to and cleaning it out that way.unfortunately there is no union so i would have to saw the pipe out and pop the leftover threaded pieces out from the elbows without a lot of room to work between pipe and ceiling. any thoughts??--nbc
  • ed wallace
    ed wallace Member Posts: 1,612
    banging rad
    you need to raise the rad to get rid of sag in pipe use tiles or wood pieces make sure vent end is higher
  • i-pipe blockage
    the radiator has been raised up 1/2 in. and slope checked.the visible horizontal run in the basement is also sloped reasonably well.
    that's why i thought of a blockage--perhaps from 1999 when i put stop leak in the old american standard to "get me through the winter"[which i did 7 more winters before puting in the new peerless 211 a!!] this riser is the first off the main from the boiler so it could have "inhaled" the boilover of the stop leak.
  • Banging riser
    Had that before. If the horiz pitch is OK, perhaps the rad is venting too quick. Have you tried slowing it a bit?
    NOT at the hand-valve(should be wide open), but the venting rate itself.
  • bob young
    bob young Member Posts: 2,177
    blow it out
    Blow out the line with CO2. did it ever work correctly ?