Glycol Derate
Jims
Member Posts: 1
Altitude usually requires a boiler outpt derate of 4%per 1000ft of altitude above 2000ft. Glycol heat transfer rate usually requires a derate of about 1/4% per 1% of Prop glycol. We normally see boiler manufacturers derating for combustion efficieny only. If the job site is at 6000 ft elevation and the 400,000 input boiler combustion efficiency is 85% and we have a 30% Prop glycol mix is the total boiler output = 400,000x(.85 effcy) x(.84Alt) x(1/4x30)/100 = 264,180 ?
0
Comments
-
Glycol
You would not derate the boiler for glycol. That is accounted for when you up-size the circulator to accommodate the flow rate needed for the glycol concentration required. The more viscous fluid will probably cause a slightly thicker boundary layer inside the boiler heat exchanger, although the higher velocity due to up-size of the circ would make it thinner. Accounting for this with any accuracy would be very difficult.
Short answer: The de-rating has been accounted for in the circulator sizing.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements