Paul, typically counter flow is pitched up-hill at roughly 1" every 10' where as parallel flow is pitched downhill at roughly 1" every 20'. That's what the books say.
Mark Z
Mark Z
0
Comments
-
counter and parallel flow?
Recently expanded 1-pipe steam system by openning and extending one of the 2" mains 30' into crawl space of our extension. All pipes are insulated w/ 2" fiber and all is running well. Slightly balancing the Rads now. While I was changing one of the the main air vents to a gorton, not on the main that had been extended, I noticed an odd thing. By using the 2" main that I was going to extendd as a guide and based on the way? she was hanging in the basement after ~70 yrs I had always assumed that I had a counter flow steam system. Looking at the other main, and a closer look at the beginnings of the extended main it is now clear that I have a parallel flow steam system. Although the main line extension was pitched as a counter flow, there issues. No water hammering, no spitting air vents..almost too good to be true. Note that originally where the 2" main ended there was the wet return. I left this in place and had the new wet return T-join in at mid-way up the pipe. This may be why I'm able to have a counter flow section function along side a parallel system. Here's the question....is it no victim-no crime or should I attempt at changing the pitch of the extended main to be a parallel flow like the system truely is. I can change the pitch without really ripping everything apart. Still can't believe I didn't see this earlier. Appreciate all thoughts and suggestions, short of getting better eyeware.
thanks, Mark Z0 -
Well, if it's working
you could justify leaving it as it is.
But I think you're going to go ahead and adjust the pitch. That's what I'd do.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
counter and parallel flow?
Steamhead, thanks and I think you're right. I'll be adjusting the pitch. Luckily the crawl space is 4' from under the floor joists to the vermin slab so I have working room. Praise the lord! Further, made the faux-pas of putting the air vent at the very end of the line. So while I'm down there I can re-pipe a touch by moving the air vent back about 12" from the end, which is max for this situation, and although the T for the air vent will be right next to the T for the last Rad riser shouldn't appear to be issue from what I've read at the Wall. Just a little more banging to keep my kids wondering who's that idiot in the basment and what? is he doing.
Thanks for advice, Mark Z.0 -
on a counter flow what way do you what the pitch going.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements