cold make up supply
[Deleted User]
Posts: 672
when would it be correct to pipe the cold make up supply water directly into the boiler return?; type of boiler? make of boiler? special piping? etc
0
Comments
-
We pipe it into the return
almost exclusively . All types of boilers . While purging , the makeup water is forced to the bottom of the boiler and any air carried with it is slowed down to be vented out . And you get the side benefit of purging the system with hot water .0 -
hmm, i sorta followed that
but can you say it in another way. because all of the piping diagrams that i find show the cold supply tied into the air separator or somewhere there abouts. and my thoughts were that it's done that way so that you'd never be able to dump cold water into a hot boiler; ie, so that the boiler, in the case of a cast iron, wouldn't be shocked/cracked. and, in the event of a failure of the prv, the boiler/return would get flooded with cold water and very shocked/cracked. ?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements