splitting existing hot water heating system into two zones

have added pellet stove to living room and due to location of thermostat back end of house gets cold due to fact that
boiler doesn't run. don't use pellet stove all the time

Comments

  • dennis setzer
    dennis setzer Member Posts: 3
    splitting existing hot water heating system into two zones

    I have hot water heating system consisting of Edwards 125K
    BTU boiler. House is approx 1400 sq ft. Boiler has a manifold. Want to split house into two zones. Bedrooms on one zone rest of the house on another . Any suggestions? thanx
  • jp_2
    jp_2 Member Posts: 1,935
    radiators

    Or baseboard?
  • kamney
    kamney Member Posts: 15
    reuse the pump

    add two zone valves - mix in an assortment of nipples and fittings - don't forget isolation/balance and purge/drain valves

    sounds like a good project for the summer!
  • dennis setzer
    dennis setzer Member Posts: 3


    all radiators are baseboard
  • Uni R_2
    Uni R_2 Member Posts: 589
    Objectives

    Dennis,

    Your boiler already seems tremendously oversized for your home. Splitting the zones will lead to shorter run times if not short cycling which will decrease efficiency and increase maintenance costs.

    What is it that is making you want to consider zoning?
  • Uni R_2
    Uni R_2 Member Posts: 589
    One idea...

    One idea might be to move the t-stat away from the pellet stove's influence and then use one or more TRVs to control temps in that area depending on how your baseboards are piped.
  • GeraBleraharyn
    GeraBleraharyn Member Posts: 1


    baseboard units are one series loop. really need to trv one unit in living room. would this require bypass for baseboard unit?