LWCO and Near Boiler Piping In-Floor Slab

rjm
rjm Member Posts: 60
Here in Mass I believe the code for new installation is; a lwco is needed when any radiation below the boiler, 400kbtu or greater or steam boiler. The latter,more than likely,does not apply. You should check your local & state code just to be sure. But it is good practice to install one anyway.
As for the piping it up and then down. it may not keep the water in the boiler. It may siphon the water right out of the boiler.

Comments

  • John_201
    John_201 Member Posts: 25
    LWCO In In-slab Radiant

    I'm a homeowner who has an incorrect installation on a 1950's in-slab system. I am trying to work with the contractor to get the near boiler piping corrected. He is going to install a Taco RMB-1 mixing block to get the boiler temps where they need to be and to modulate the temp to the floor correctly. Through all this hassle I have researched quite a bit both here and on other sites.

    He says that a LWCO is not necessary. As the system is currently piped it is sending supply water out through the large pipe instead of sending it immediately to the floor through the manifold. Shouldn't the supply go to the manifold and the return be through the large pipe? It seems that sending the supply through about 15 feet of pipe before it gets to the floor is a waste of heat.

    Doesn't good and safe practice call for the LWCO?

    Thanks, John
  • mark o
    mark o Member Posts: 12
    lwco

    lwco are code in pa , also the gas shutoff valve you have that is reused , we are required to change out
    Mark Overly.
  • tim smith
    tim smith Member Posts: 2,807
    Here in Seattle

    We are required to put lwcos w/ test button and manual reset on boilers, also manual reset limits. Just depends on location. As far as mod mixing, did he include it in your bid? If the boiler can't run down to safet floor temp levels due to boiler protection then he needs something to mix down, could be as simple as and mech. tempering valve or as elaborate as motorized mixing w/ reset or injection w/ reset. All depends on boiler requirement and what he included. I would think at least the thermostatic mix valve would be the least to be done. Tim
  • kpc_9
    kpc_9 Member Posts: 11
    why not...

    in todays world the extra measure will cover your behind. Especially in a older slab set up... Seems strange anyone would not want that. Does he know how to wire it so it works? Also the Pressure relief valve needs to be repiped ...it is bushed down to 1/2"...that is a no-no. kpc
  • fatty_2
    fatty_2 Member Posts: 54


    ... i don't see any gas shutoff at all?
  • John_201
    John_201 Member Posts: 25
    Answers To Your Questions

    He has a Taco RMB-1 on order that should be in on Monday and recognizes that he needs a plumber to correct the install. I have found out that code in Indiana is to install per manufacturer instructions. This has to be plumber who has experience with fairly complicated piping not just a wax ring replacer. The Dunkirk manual is very clear that a LWCO is required any time the radiant level is below the boiler.

    He has agreed to correctly size the pressure relief valve piping and cut the threads off the end so it can't be capped.

    The boiler gas valve is out of view but present.

    I think the Taco LWCO LTR with reset is what I will insist on.

    One final question. Should the to floor output of the RMB go directly to the manifold next to the boiler in the picture?
    Thanks
  • mikea23
    mikea23 Member Posts: 224
    LWCO

    LWCO on that gas boiler is very simple if you buy a gaurd dog by Mcnld Miller it has a wire harness that simply plugs into your boiler. Code or not no hydronic system should be without one.
  • mark o
    mark o Member Posts: 12
    gas v

    the gas bv I was referring to is the repiped one to the water heater.( new teflon tape)
    Mark Overly.
  • John_201
    John_201 Member Posts: 25


    There is on on the water heater but it can't be seen in the photo. Thanks