Condensate Volume of Mod-Con
Options
Mike T., Swampeast MO
Member Posts: 6,928
25 cubic feet per hour of natural gas was steadily consumed during a 16 hour period.
Continuous, steady fire with flue temp average of 93° (±2°F) during the period. Mainly nighttime, cloudy with temp nearly steady and average of 32°F and RH 80% during the period.
400 cu.ft. = 11.33 cu. meter
Theoretical condensate volume of 11.33 cu.meter @ 1.53 kg/cu meter:
11.33 * 1.53 = 17.33 kg (38.2#, 4.6 gal) theoretical condensate
Condensate produced: 12.86 kg (28.35#; 3.4 gal)
á = 0.74 (á = theoretical / actual condensate)
Unrecovered condensate volume:
38.2# - 28.35# = 9.85#
Does this mean?
93°F flue - 32°F outside air temp = 61°F difference
61 * 9.85# = 600.85 <I>maximum unrecovered condensate BTUs<B> during a 16-hour period</B></I>
With the only boiler losses remaining...
Absolute temp rise of combustion air
plus
The jacket????
Here are some additional measurements made during nearly identical conditions (both quite steady):
Incoming air temp: <B>69°F</B> (test fitting of Viessmann concentric flue) triple verified--opening slide coupling caused temp to drop as expected assuming the 5' horizontal flue was significantly heating the incoming air. 55°F ambient air temp in basement near boiler.
Flue temp @ outlet (outdoors): 89°F
Combustion Air Loss @ 10% excess air
400 * 11 = 4400 cubic feet of combustion air
raised from 69°F to 93°F = 24°F delta-t
@ 0.018 btu per cuft/°F heat capacity of dry air
4,400 cu.ft. @ .08 cu.ft./pound = 352# combustion air
latent heat at about 50% RH = about 7 btu/pound ??? (Brad White??) (outdoor air 32°F; 80% RH; combustion air @ boiler 69°F; temp at outlet 89°F) [value changed from 10 btu/pound]
352 * 7 = 2,464 btu <I>latent flue gas heat loss</I>
4400 * 24 * 0.018 = 1,900 btu <I>flue temperature loss</I>
400,000 btu consumed
- 2,464 btu latent flue temp loss ????
- 1,900 btu flue temp loss
<U>- 601</U> btu condensate loss
= 395,035 btu utilized = 98.8% boiler efficiency????
Continuous, steady fire with flue temp average of 93° (±2°F) during the period. Mainly nighttime, cloudy with temp nearly steady and average of 32°F and RH 80% during the period.
400 cu.ft. = 11.33 cu. meter
Theoretical condensate volume of 11.33 cu.meter @ 1.53 kg/cu meter:
11.33 * 1.53 = 17.33 kg (38.2#, 4.6 gal) theoretical condensate
Condensate produced: 12.86 kg (28.35#; 3.4 gal)
á = 0.74 (á = theoretical / actual condensate)
Unrecovered condensate volume:
38.2# - 28.35# = 9.85#
Does this mean?
93°F flue - 32°F outside air temp = 61°F difference
61 * 9.85# = 600.85 <I>maximum unrecovered condensate BTUs<B> during a 16-hour period</B></I>
With the only boiler losses remaining...
Absolute temp rise of combustion air
plus
The jacket????
Here are some additional measurements made during nearly identical conditions (both quite steady):
Incoming air temp: <B>69°F</B> (test fitting of Viessmann concentric flue) triple verified--opening slide coupling caused temp to drop as expected assuming the 5' horizontal flue was significantly heating the incoming air. 55°F ambient air temp in basement near boiler.
Flue temp @ outlet (outdoors): 89°F
Combustion Air Loss @ 10% excess air
400 * 11 = 4400 cubic feet of combustion air
raised from 69°F to 93°F = 24°F delta-t
@ 0.018 btu per cuft/°F heat capacity of dry air
4,400 cu.ft. @ .08 cu.ft./pound = 352# combustion air
latent heat at about 50% RH = about 7 btu/pound ??? (Brad White??) (outdoor air 32°F; 80% RH; combustion air @ boiler 69°F; temp at outlet 89°F) [value changed from 10 btu/pound]
352 * 7 = 2,464 btu <I>latent flue gas heat loss</I>
4400 * 24 * 0.018 = 1,900 btu <I>flue temperature loss</I>
400,000 btu consumed
- 2,464 btu latent flue temp loss ????
- 1,900 btu flue temp loss
<U>- 601</U> btu condensate loss
= 395,035 btu utilized = 98.8% boiler efficiency????
0
This discussion has been closed.
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 48 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements