fire eye
fwb1375
Member Posts: 7
can anyone tell me how to test a fire eye? i tried to get ahold of honywell,only for them to tell me that i need to ask my distribtor. funny thing is my distributor gave me honeywells 800# because they could answer me.
0
Comments
-
Our supplier, Commercial Heating in Bridgeport, CT, has a test panel. They screw the unit to the tester and use a set of switches to see if everything is working to spec.
Or do you mean the sensor?0 -
Regarding fireye and testing
What is happening with the control. Does it go into pre purge for appx 90 seconds and then energize the pilot solenoid and ignition transformer, if it gets this far and then goes off on flame failure, most likely you have a poor flame signal. Sometimes a bad UV eye or amplifier too. If it just stays in pre purge and never tries to go to pilot or ignition, then probably a bad purge card. Many other things to evaluate if not the above. post what is the sequence of operation currently. Is this a UV amplifier or rectification. What type of amplifier is on fireye control. Tim0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements