BASEBOARD ZONE
Options
Bruce Marshall
Member Posts: 37
Mike,
I would use a Taco SR501 to control the pump with power from 4 N/O & neutral and a Honeywell L4006A wired with one leg in series from 5 & 6 N/0 to T T. Set the L4006A to 180 degrees max so you won't produce steam.
Bruce Marshall
I would use a Taco SR501 to control the pump with power from 4 N/O & neutral and a Honeywell L4006A wired with one leg in series from 5 & 6 N/0 to T T. Set the L4006A to 180 degrees max so you won't produce steam.
Bruce Marshall
0
Comments
-
BASEBOARD ZONE
Which model/type aquastat & switching relay would you use to control a baseboard loop off a steam boiler? thanks for your help guys0 -
baseboard zone
Thanks for the imput Bruce, sounds good0
This discussion has been closed.