boiler with fan coil
Hi Wayne,
How about an aquastat on the supply to the fan coil, cutting out the blower before the supply temp. gets too low.
Guy
  • Wayco Wayne_2
    Wayco Wayne_2 Member Posts: 2,479
    I got a call from
    a customer from 2 years ago. I installed a boiler with 2 fan coils. A problem happens when there is a call for heat and someone is taking a shower. Since the boiler goes into priority on a call from the indirect water heater for domestic hot water the fan coils have no hot water and blow cold air until the indirect is satisfied. I guess I could run the fan relays through a remote bulb sensor to shut off fans until the hot water returns to the coils. Any other suggestions? WW
  • tim smith
    tim smith Member Posts: 2,886
    Aquastat on return line
    Put the aquastat on return line so coil is hot before fan comes on. Set it at appx 100 degrees on and 15 degree differential. Watch out for too low of supply temps to coil causing short cycling. Good luck, Tim
  • MechTech_2
    MechTech_2 Member Posts: 84
    Summeraire
    Summeraire came out with an air handler with that exact strategy built in. Finally!! An aquastat detects a drop in water temperature, and stops the blower. When the aquastat detects a higher water temp, the blower starts again. We haven't put one in yet, but it will prevent alot of callbacks.
    Al
  • joel_19
    joel_19 Member Posts: 933
    KISS
    Loose the priority!!!!!! you probabaly don't need it if you've got enough tank so what if recovery is longer as long as you don't drain it which they may never do.
  • MechTech_2
    Big Load
    Your right! Most times you can probably get away without the priority. I got burnt when the air handler load was high enough to have an effect. Do the math, and apply the technology appropriately.
    Al Crawford
  • Wayco Wayne_2
    The boiler is
    a prestige from TT. Can I turn off the priority? I don't think so. WW
  • don_185
    don_185 Member Posts: 312
    Next time
    Put in a oil furnace. Why have a boiler that has to heat the water then, the water has to heat the air.
    Opps I forgot, this is a wethead site.
  • tim smith
    Regarding fan coil & indirect
    I would not shut off priority, use the aquastats on return lines and that will cure problem.
    EBEBRATT-Ed Member Posts: 19,574
    I agree use an aqustat to shut down the fans. The complaint isn't lack of heat--just cold air blowing on them. Stop the cold air blowing--they will still have domestic hot water and will not miss the heat being off for a short time.
    ED
  • Darrell_3
    Darrell_3 Member Posts: 7
    aquastat applications
    I am in need of some model numbers for an aqua stat that will turn a fan on when the temperature rises. What are some that you have used with success? I don't need a high limit application...Ross
  • Darrell_3
    proper aquastat
  • Randy-Lee Braman
    Randy-Lee Braman Member Posts: 40
    honeywell
    A Honeywell L6006c Tradeline would be a good one,can be used for temp rise or fall.
    Randy
  • Uni R_2
    Uni R_2 Member Posts: 589
    Relay
    What about putting a simple relay on the DHW circ, so that whenever it starts, it shuts off the air handler? Likewise, when the DHW call is finished, the air handler starts right back up.