21\" 3-column EDR

steve_173
Member Posts: 140
I have some 21" 3-column radiators that I need an EDR for. The tables seem to only have 18" and 22" for 3 column. Does this indicate that only 22" were made and I am measuring incorrectly? Are there more expansive tables?
How do I calculate the EDR just from the dimensions of the radiator?
How do I calculate the EDR just from the dimensions of the radiator?
0
Comments
-
steve
Allow 3 sq. ft. per column, and you should be OK.
The slight difference is negligible.0 -
Thanks. Just to be doubly sure since I may have to argue about it. 2.25 is too low?0