hot air heater loses it prime when oil tank gets below 1/4 tank
Big Ed_4
Big Ed_4 Member Posts: 3,226
You have a leak at the burner assuming you have a gravity feed from the oil tank. It should be easy to find. Look for the oil leak. Since the burner mounts high on the furnace.When the oil drops oil below the leak it starts to suck in air and when the level is higher then the leak it will leak oil. Just look for the oil leak.
Jim, if a check valve was used it would only add more restriction to the oil flow . If you add restriction more air will be sucked in. Check valves are useless to correct air leaks they are only good to control flow direction which is not needed on just about all oil supply systems. Hope this helps.......
  • mark pagliarini
    mark pagliarini Member Posts: 1
    oil heater loses its prime
    my hot air heater is about 5 years oil but from the time it was put in when the oil tank gets below a 1/4 of tank the heater will lose its oil prime the reset button on the oil burning unit popps up I then have to opean the bleeder on the burner and push the reset button. the burner unit doese sit higher than the oil line coming into the burner and Iam guessing this is the problem but I dont think any one noes of a fix. thanks for you help mark
  • burnerman_2
    burnerman_2 Member Posts: 297
    2 choices
    add a return line or as a lot others will add a tigewr loop it can be added then u only filter the oil u use or # 3 keep the tank over 1/4 fuu good luck royboy
  • Jim_61
    Jim_61 Member Posts: 3
    Install a check valve near the tank, and check that the packing nut on the valve at the tank in snug.
    Jim ...
  • ARTIEGEE
    ARTIEGEE Member Posts: 3
    lost prime
    An air leak in the oil line at the burner or above is causing the loss of prime. Fittings (should be flared), fuel unit seal at shaft and plugs in the fuel unit not doped are the usual suspects. Check valves, tigerloops and 2-pipe sytems only mask the problem. It has to be properly repaired to prevent oil stream foaming which can result in incomplete combustion. The integrity of the line can be checked with a vacuum guage. Oil line leals below the burner will show oil spots.
  • bill nye_3
    bill nye_3 Member Posts: 307
    Don't
    Don't let it get below a quarter tank and you won't have to blead it
  • Leo
    Leo Member Posts: 772
    What Kind
    What kind of burner is it, a Riello?
    Leo