steam help needed
STEVEN MARKS
Member Posts: 154
I am presently investigating steam probelms in a 24 unit apartment building.
I have replaced some disc traps,radiator valves, lowered the pressuretrol setting and now have most of the radiators working coreectly.
All but 3 are now working. I have replaced the traps. If I open the trap at the radiators and start the boiler the radiators will get hot. I then tested the condensate returns by disconnecting the traps and filling the condensate returns with water. All seem to be draining correctly.
Long term tenants tell me these radiators have never worked.
The boiler is located in the center of the building with 2 steam mains running the length of the building in opposite directions.
There are no main air vents at the end of mains. At the end of each main is a 3 x 1/2" tee that goes to a thermostatic trap (above the mains). This is the condensate return line for all the radiators.
There is not a F&T trap at the end of the mains. The pipe elbows to the floor. Essentially 2 condensate returns. 1 overhead and 1 at floor.
I have replaced some disc traps,radiator valves, lowered the pressuretrol setting and now have most of the radiators working coreectly.
All but 3 are now working. I have replaced the traps. If I open the trap at the radiators and start the boiler the radiators will get hot. I then tested the condensate returns by disconnecting the traps and filling the condensate returns with water. All seem to be draining correctly.
Long term tenants tell me these radiators have never worked.
The boiler is located in the center of the building with 2 steam mains running the length of the building in opposite directions.
There are no main air vents at the end of mains. At the end of each main is a 3 x 1/2" tee that goes to a thermostatic trap (above the mains). This is the condensate return line for all the radiators.
There is not a F&T trap at the end of the mains. The pipe elbows to the floor. Essentially 2 condensate returns. 1 overhead and 1 at floor.
0
Comments
-
Sounds like a Vapor system
when you opened the traps, did any air come back at you from the return line?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Steam
No. When I opened the traps no air. The radiator slowly began to heat. I tested the drains and they seem to be working. I earlier posted this is 24 apartment but it is only 12. This is an older Mills boiler and I found to be fired at only 2 gph. I am thinking maybe it is underfired?? Does this sound possible? Steam boiler to small so not all the radiators heat? The condensate returns never seem to get warm.0 -
Could be
what is the boiler's rating, and how is it being fired (burner type, lo-hi-lo?)?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
If, when you open the traps on the three radiators
that aren't heating correctly, and the radiators then get hot, it indicates that those traps, new or not, are plugged. Also, see that your pressure is next to nothing. I once heated a row of fourteen greenhouses with the gauge reading zero pressure (and the gauge worked)!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements