[Deleted User]
Posts: 2
No matter how many grounding wires you have in the box, all together, they count as a single "wire" for purposes of calculating conductor box fill.
Since you mention #12 and #14: if you've got different sized wires in the box, you count the single ground wire as though it was the largest wire in the box.
Since you mention #12 and #14: if you've got different sized wires in the box, you count the single ground wire as though it was the largest wire in the box.
0
Comments
-
when looking at....
a j-box...it will say how many conductors can be in that box....#12 and or #14...is this # just neutrals and hots or does it also include ground wires? ty,kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I'm pretty sure it does.0 -
-
Get a copy of
The 2002 / 2005 NEC. It will list approved number of conductors in any box or situation. Or check out mikeholt.com.0
This discussion has been closed.
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements