Steam Main Vent Sputters

Sizzlaw
Member Posts: 11
I don't see any pressure adjustment on the boiler. It's an old "Arcoliner" with a Beckett oil burner.
The vent is about 3 inches from the downturn of the main.
I didn't have the continuous sputter until this winter; it seemed to be ok all of last winter.
The vent is about 3 inches from the downturn of the main.
I didn't have the continuous sputter until this winter; it seemed to be ok all of last winter.
0
Comments
-
Main Vent Sputters
(I posted this yesterday but used the wrong words.)
ONE-PIPE STEAM SYSTEM, OLD. 2-inch pipes. New main vent installed a year ago. Now continually sputters, doesn't close. Boiler pressure was 3.5 psi. Replace vent? Any special type? Vent is hard to get at. Please help. Thanks.
0 -
Pressure
First set the pressuretrol to 0.5 psi cut in and 1.5 cut out.
Second is your vent located at the end of the main?
0