Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Steam Main Vent Sputters
Sizzlaw
Member Posts: 11
I don't see any pressure adjustment on the boiler. It's an old "Arcoliner" with a Beckett oil burner.
The vent is about 3 inches from the downturn of the main.
I didn't have the continuous sputter until this winter; it seemed to be ok all of last winter.
The vent is about 3 inches from the downturn of the main.
I didn't have the continuous sputter until this winter; it seemed to be ok all of last winter.
0
Comments
-
Main Vent Sputters
(I posted this yesterday but used the wrong words.)
ONE-PIPE STEAM SYSTEM, OLD. 2-inch pipes. New main vent installed a year ago. Now continually sputters, doesn't close. Boiler pressure was 3.5 psi. Replace vent? Any special type? Vent is hard to get at. Please help. Thanks.
0 -
Pressure
First set the pressuretrol to 0.5 psi cut in and 1.5 cut out.
Second is your vent located at the end of the main?
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements