Be very carfull where you drill! most T.J.I manufactures are very specific on where you can penetrate. Typically 18" from load bearing wall (inside of foundation) and whatever size hole you drill you have to be 6x the diamater to the next hole
however, you can make a hole as BIG as you want as long as you leave 1/4" on top and bottom. After having to pay for a replacement TJI, I always check with th G.C. or homeowner and have them ok every hole to be drilled, Pryor to spinning the steel!
Al
however, you can make a hole as BIG as you want as long as you leave 1/4" on top and bottom. After having to pay for a replacement TJI, I always check with th G.C. or homeowner and have them ok every hole to be drilled, Pryor to spinning the steel!
Al
0
Comments
-
Staple Up
Does any one here in a crwal space not drill holes in BCI/TGI's and loop under to the next bay.0 -
it is a crawl space....
my saying is .."I like to keep my work up."
you do what you have to do when planning has been thrown to the wind...0 -
IMO
It is easier to drill the holes then not have to insulate the loops that drop under the insulation between the TGI.
Mike C.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
It takes a bit more tube and
looks un-professional to loop under the joists, in my opinion. Even in a seldom seen location
Generally an 1-1/2" hole can be drilled anywhere in the web of a I joist. Plenty for two runs of 1/2" pex to fit in.
Always best to check a hole drilling chart for the I joist you use. Some manufactures are now sticking these charts on the joist for the installers to use.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements