raypac pool heater

Options
D lux_2
D lux_2 Member Posts: 230
Installer NOT me didnt wire motor for inducer for 110 V factory wired for 220 V motor wouldnt turn fast enough to move switch

Comments

  • D lux_2
    D lux_2 Member Posts: 230
    Options
    anybody work on raypack pool heaters?

    haveing powervent not closing pres. switch D2 power vent thanks
  • Ed_26
    Ed_26 Member Posts: 284
    Options
    Raypak pool heater

    Assume gas fired? Are you qualified to work on this? If not, you should call a pro. That said, check the sensor tube & ventor wheel for debris/blockage.
  • jim lockard
    jim lockard Member Posts: 1,059
    Options
    mag gauge

    Check your pressure switch with your mag gauge if in spec. change the switch if not change the powervent.
  • Empire_2
    Empire_2 Member Posts: 2,343
    Options
    Motor,..

    Might want to replace it Now since it probably ran so hot and damaged the windings as a result. Also as a quick refference, Your amp probe would have giving you the answer if you used it,...

    No dis... intended:-)

    Mike T.