steam boiler sizing

Jim_83
Member Posts: 67
I am replacing a steam boiler heating a 2 story house with attic. The boiler will be heating the second floor and attic. The first floor is a separate apartment and has its own steam boiler.
My question concerns the boiler sizing. From reading the posts I know it is very important to size a steam boiler based on the connected load.
The connected load is 180 square feet steam. There is a boiler rated at 158 square feet steam and the next size is 271 square feet steam. I know the rule is to pick the next size higher, but in this case, is 271 sq ft too big a boiler. Would I be better off with 158 square feet steam boiler? The boiler will be gas fired.
What are the options?
My question concerns the boiler sizing. From reading the posts I know it is very important to size a steam boiler based on the connected load.
The connected load is 180 square feet steam. There is a boiler rated at 158 square feet steam and the next size is 271 square feet steam. I know the rule is to pick the next size higher, but in this case, is 271 sq ft too big a boiler. Would I be better off with 158 square feet steam boiler? The boiler will be gas fired.
What are the options?
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements