Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Teledyne Larrs Pool Heater
helpingothershelpthemselves_2
Member Posts: 326
Last night I was asked to troubleshoot a problem with a brand new 400,000 BTU Laars oil fired swimming pool heater with a Beckett with 7184B Relay. Upon visual inpsection , I noticed the burner did not have a clean cut type pump(no solenoid), but the burner was packaged with 7184B cad cell relay. So as you can imagine during pre purge, flame was sensed by the cad cell relay thus sending the relay into safety.
My wonder is ...... how can we assure that packaged units, will in the future, have proper selection of relay and fuel unit either by the pool heater manufacturer or Beckett, before the unit is in stock at the wholesaler ?
My wonder is ...... how can we assure that packaged units, will in the future, have proper selection of relay and fuel unit either by the pool heater manufacturer or Beckett, before the unit is in stock at the wholesaler ?
There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements