in, ' a pocketful', dan says;

and any buried steam or condensate lines, it pays to install an inexpensive water meter on the feed line."

does anyone know the specifics of the meter that he's refering to, or do yous have a suggestion?

Comments

  • Robert O'Connor_12
    Robert O'Connor_12 Member Posts: 728
    Feeder

    Try this!



    http://www.hydrolevel.com/pages/products04b.html



    Robert O'Connor/NJ
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,598
    Yes,

    that's a good choice. I wrote the book before that product arrived.
    Retired and loving it.
  • and,

    can that be applied to hot water also?
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,598
    A hot water system

    shouldn't be taking on any fresh water. It's a closed system. It needs a low-water cutoff to guard against leaks.
    Retired and loving it.
  • taking on fresh water

    and that's exactly what i keep telling the knuckleheads that i'm dealing with, but our boiler pro?, he's got? me by experience, has it in his head that leaving the supply water on is the way to go. which brought up the discussion
    of metering the water to see if there's a leak. and pro feels more comfortable with a leak/flood damage vs a lwco that could fail, because the high limit could fail at the same time. grrrrrrrr!
  • Timco
    Timco Member Posts: 3,040


    12 psi and a steady leak is a TON of water in a short time. If the supply is off and there is a leak, there will be a drop in pressure that the LWCO will catch. Simple as that. The supply can be left on after a new install to makeup as air is expelled, but is typically not needed after a short while.

    Tim
    Just a guy running some pipes.
  • ton of water

    here's a chart that, if i'm remembering correctly, came from a course at york shipley

    IT'S JUST A SMALL LEAK

    gals/hr gals/mo gals/yr

    1-2 drops/min .004 3 35

    1-2 drops/sec .05 36 438

    intermittant .9 657 7,887
    stream

    1/16" stream 3 2,191 26,292

    1/8" stream 10.2 7,449 89,391