Makes you think
Jeff Lawrence_25
Member Posts: 746
At my daughters school. The principal called and told me there was no cooling in the cafeteria and could I look at it. Sure!
I was more than a few miles away, so I called my 17 year old daughter and asked to do a visual check. The outside fan was running and so was the inside blower. Suction line was barely cool.
Hmmm.
Got there and saw the exact same thing. Compressor was warm and the one next to it was slightly warmer, but neither was running. Got the Fluke out and read voltages. L1-L2 240v L1-L3 240v L2-L3 nothing (3 phase). The condensers are the only 3 phase equipment at the school.
Looked up at the transformers on the pole nearby and saw a fuse was blown.
When the power company came out to replace the fuse on the transformer, there was a loud POP. oops, bad transformer. The kids got out the rest of the day so the power company could replace the transformer.
Interesting stuff, this HVAC work.
I was more than a few miles away, so I called my 17 year old daughter and asked to do a visual check. The outside fan was running and so was the inside blower. Suction line was barely cool.
Hmmm.
Got there and saw the exact same thing. Compressor was warm and the one next to it was slightly warmer, but neither was running. Got the Fluke out and read voltages. L1-L2 240v L1-L3 240v L2-L3 nothing (3 phase). The condensers are the only 3 phase equipment at the school.
Looked up at the transformers on the pole nearby and saw a fuse was blown.
When the power company came out to replace the fuse on the transformer, there was a loud POP. oops, bad transformer. The kids got out the rest of the day so the power company could replace the transformer.
Interesting stuff, this HVAC work.
0
Comments
-
You should have seen
what happened in one of my buildings when "B" phase blew...was undersized, 20a. pole fuse for 2 16k s.f. buildings...lost VFD's, elevator controllers, etc...was not a pretty sight!0 -
You should have seen
what happened in one of my buildings when "B" phase blew...was undersized, 20a. pole fuse for 2 160k s.f. buildings...lost VFD's, elevator controllers, etc...was not a pretty sight!0 -
Round 2
They replaced the transformer all right.
They wired it wrong.
L2 to ground was about 440 volts
L1 to L2 was 327.
The school wondered why I turned the breakers off on the condensers.
arrggghhhhhh
Oh, I've seen high rise buildings single phase. True, it's not a pretty sight.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements