Pex through a fire wall
Aidan (UK)
Member Posts: 290
> I <BR>
> know there are sleeves made for electrical that <BR>
> has a foam in it that expands when exposed to <BR>
> heat. I was thinking there might be something <BR>
> like that for pex. <BR>
<BR>
There is.
Google for "intumescent collars" or "intumescent sleeves".
Something like these;
http://www.astroflame.com/intumescent_pipe_collars.html
> know there are sleeves made for electrical that <BR>
> has a foam in it that expands when exposed to <BR>
> heat. I was thinking there might be something <BR>
> like that for pex. <BR>
<BR>
There is.
Google for "intumescent collars" or "intumescent sleeves".
Something like these;
http://www.astroflame.com/intumescent_pipe_collars.html
0
Comments
-
What should be used for fire stop on Pex tubing going through a fire wall?0 -
now that sir would depend upon how many hour fire wall
assembly one was threading the pex tubing through...0 -
oops
It's a 2 hour rated wall.0 -
Run Pex thru iron pipe?
Run the PEX thru a short piece of larger black (or galv) iron pipe thru the firewall and firecaulk the iron at the wall on both sides and the PEX to the iron at one end only?0 -
I'll have to run that one by the inspector. Of course, I think the guys already ran the Pex. I know there are sleeves made for electrical that has a foam in it that expands when exposed to heat. I was thinking there might be something like that for pex.0 -
Best of luck
i had firewall issues at my new building; what a pain! if push comes to shove you may need to have an engineer sign off on it!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
pex and firewall
I think Uponor aquapex is plenum rated by itself. It may not need to be sleeved. Although I think there is a minimum separation distance between two pieces of pex.0 -
Thanks Everyone
I contacted the Pex manufacturer. They emailed me a cut sheet that shows the proper way to just use fire caulk and maintain the 2 hour rating. We'll present that to the inspector and go from there.
Thanks again.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements