One- pipe steam main valve sputters

Sizzlaw
Sizzlaw Member Posts: 11
One-pipe steam system, old. 2-inch pipes. New main valve installed a year ago. Now continually sputters, hisses, spits, doesn't close. I did notice the boiler pressure was 3.5 psi. Replace valve? Any special type? Valve is not adjustable and is hard to get to. Small house, eight radiators. Help, please.

Comments

  • ed wallace
    ed wallace Member Posts: 1,613
    main valve sputers

    have the pigtail cleaned and make sure the pressureteol is turned down as far as possible