T&P valve still drips after replacement on boiler

Empire_2
Empire_2 Member Posts: 2,340
20 psi,....Huhhhh. are you sure that is accurate? I cant tell you how many times I have found either a little off and way off the actual pressure. If you need service call some one or you can drain boiler and see if the gauge zeros out. Could also be a leaking through PRV.

Mike T.

Comments

  • Jonni
    Jonni Member Posts: 2
    T&P valve still dripping after replacement on boiler

    All

    I have a Peerless wbv4 and noticed my T&P was dripping constantly.

    I replaced T&P and water is still dripping.

    Any ideas other than it being a 'bad' new T&P??

    Boiler is @ 20lbs PSI

    Thanks
  • John McArthur_2
    John McArthur_2 Member Posts: 157


    Have you checked the expansion tank? If the bladder loses air side pressure the relief will discharge every time the boiler heats up. Sorry if you already know this.
  • scrook_2
    scrook_2 Member Posts: 610
    T&P?

    Should be just a pressure relief on a boiler, vs. Temp & Press on a water heater -- in any case I'd suspect the gauge reads low but could be a lot of crud in the boiler water and you got a piece embedded into the new relief valve? What happens if you drop the pressure to 15 psi? How high's the top radiation from the boiler?
  • Jonni
    Jonni Member Posts: 2
    Good thought Mac

    I will change out the expansion tank. One question I have is when I drain the boiler down to 0 and change out the tank do I have to worry about the cold water supply 'shocking' the sections and potentially cracking one.

    Basically what is the rule of thumb when draining the boiler down and pressurizing it back up?

    Thanks
  • Tinman1
    Tinman1 Member Posts: 3


    Read "pressure relief valve blows off" from a previous post.
  • Jerry_15
    Jerry_15 Member Posts: 379


    Pressure on the tank needs to be the same as the operating pressure of the system. Common screw up: Ex tank replaced with domestic ex tank pre-charged to 60 psi. How do you know? Dom tank has 3/4 thread, hydronic tank has 1/2". How do you fix it? Let air out of the tank and check it with a tire gauge until it's at 15 psi.
    If it's the right tank and there's no pressure or water comes out, replace it. Turn the water feed off first.