steam intall/

you have a nice bit of clear height above that boiler. A proper header and equalizer over good initial boiler risers will make for some very nice, dry steam. Skimp not and ye shall be well served. Don't blow it.

Comments

  • Kman
    Kman Member Posts: 13
    correct install?

    Attached are pictures of a current install of a weil-Mclain eg 45 steam unit. Anything inherently wrong?
  • ed wallace
    ed wallace Member Posts: 1,613
    steam piping

    wheres the hartford loop? looks like the installer hasnt read the install manual
  • Kman
    Kman Member Posts: 13


    just to follow up. It looks like the equalizer return is going to come from the ell on top of the tee going to the main. Is that right? Will condensate go up? Should I stop them now?
  • Kman
    Kman Member Posts: 13


    They haven't got that far, but a hartford loop is planned. I am concerned about a lack of a header.
  • ed wallace
    ed wallace Member Posts: 1,613
    steam install

    the installers need to read the install manual stop them now no header no hartford loop
  • David Nadle
    David Nadle Member Posts: 624
    Might be OK but get the manual and do it right.

    If that elbow at the top is going to head back down to an equalizer and the wet parts are piped correctly and you have a wet return somewhere that isn't in any of the pictures, then I think what you'll have could be functionally equivalent to the recommended piping.

    But why take a chance? Download the manual from weil-mclain.com and insist that they follow the diagram. It's not like it's more complicated than what you have now. On the bright side, at least they're using steel.
  • ed wallace
    ed wallace Member Posts: 1,613
    boiler install

    David how can you say it might work? the customer is paying a company good money he deserves a properly installed boiler
  • your gonna be cold....

    Stop them now. Not even close. Your gonna be cold a bit longer.
  • gerry gill
    gerry gill Member Posts: 3,078
    not even close

    to a proper install..as others have said, ''read the manual''..

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Daniel_3
    Daniel_3 Member Posts: 543


    Absolutely agree!
  • kev
    kev Member Posts: 100
    If you

    Look close, the manual is on top of boiler and open.
  • Kman
    Kman Member Posts: 13


    They have since undone the suspect work which killed a half day and came up with another plan.
    Another cold night!
  • David Nadle
    David Nadle Member Posts: 624
    Agreed. Install it properly.

    I did say they should follow the install guide. But why exactly wouldn't it work? If you look at what was done so far, the only thing really different would be where the main is connected, into the riser instead of into the short horizontal run back down to the equalizer. Does the steam know vertical from horizontal?

    The existing riser is plenty long. If I can assume that nearly all the condensate returns by a different path than back down the main--and I did ask if that was true--I think it might work OK. But, as I said, he still shouldn't do it that way.

    Of course, I could be very badly, stupidly wrong. If so, let me have it.

  • Brad White_184
    Brad White_184 Member Posts: 135
    The Why

    The reason it would not work as advertised is that the initial riser will draw up condensate with the steam. Sure the height works but half the height is spent with water falling back against an upflow of escaping steam.

    Steam knows vertical from horizontal when water is involved. Well, OK, the water knows and it is parasitic.

    The better approach as you know would be to turn horizontal to a header and roll that to the equalizer. The water goes back to the boiler much as a judo master rolls an assailant using his momentum. The dry steam is free to rise, leaving the fight behind.