Buffer tank answer to short cycle boiler
Bobcat_2
Member Posts: 8
New installation of 5-6,000 sq.ft. of entry and pool deck snowmelt at a resort. 1MMbtu copper finned tube, on-off (wish I would have ordered a two stage) that creates heat very quickly but my temar 664, two zone injection control does not delver the heat fast enough due to boiler protection and cold start up I suppose. Would a buffer tank, say a 120 gal, connected in series in the primary (boiler) loop extend firing and minimize short cycles? I've never used a buffer before. Siggy shows a seperate pump, etc, when other loads are connected. This is a stand alone system. If the buffer and connecting piping reaches adjusted limit at 160 degrees, then am I back to square one? Maybe spread the on-off differential? Any ideas out there to create a successful installation? Cold toes in Oregon.
0
Comments
-
what size pumps.
are you getting enough flow through the boiler. what size is the injection line? What size are the pumps? What are you protecting the copper fin tube boiler from? There should be no bypass required for water temp. just for high flow. Check the install guide. How is it piped?
You might not need a buffer tank at all.0 -
With that much snowmelt
that boiler should run pretty much non stop, if all the pipes and pumps are sized correctly I'd guess you provide 125- 130 btu/ square foot of slab.
If you have a two zones and the potential for one to call expect some cycling. a 1 million BTU boiler running 80% efficiency plus any altitude derate =??
Check the numbers to be sure you have enough tube in the slab to move about 800K, then the pipe size to handle the needed flow rates, and the pump capacity to drive it all. Remember about the derate for the glycol mix when sizing.
A properly placed buffer could help, a mod con boiler would be better
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements