Zc/Zr unorthodox control set boss' request
Options
Jim_64
Member Posts: 253
Thanks for the imput Boss went to vermont and I did not want to bother him. Thanks for helping the green mechanic
0
Comments
-
help on control issue stuck in the middle
The client wants a 4ft piece of C/I baseboard and a runtal radiator to heat when three zones call but not when the indirect calls. It was piped it in an old fashion two pipe feed and return. I went ther because it was heating on gravity flow (no flow check) it was not hot just warm. My boss had me install a 3/4 taco sweat check. This "demizone" heated well before the check was installed, powered by the circulators on the other 3 zones. To day he sends me with a taco 005 and tells me to install a single zone relay jump jump tt on new relay and power the relay from ZC/ZR on the existing taco four zone relay pack. will this work the oil guy says it will not boss says it will.0 -
larry, sorry , but I think the boss is right
I would need to look it up, but I think it goes like this, ZC is powered when cir is powered and ZR is powered when above low limit of control. Check out fact sheet on a L8124A which will show ZC / ZR and 845 relay wiring spec's0 -
You should be able
to integrate a single Taco relay into the 4 zoner . Taco has detailed wiring diagrams on their website . I know you can do it that way with ZC / ZR , using the single relay as the priority zone . Rewire the indirect into the single relay and you'll be set .0 -
zc
John, it worked just like you and the boss said it would thanks again0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements