Working on the Knight moves
Steamhead (in transit)
Member Posts: 6,688
that's fine work!
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
dos 210 wall hungs
in a commercial shop. Still need to run condensate lines, finish wiring, maybe insulate, or maybe leave bare copper?
hot rodBob "hot rod" Rohr
Living the hydronic dream0 -
Looks nice,
but Bob Segar woul;d be confused. WW
Looks Good, Hot Rod
Nice work, HR. Is that a Honeywell air sepator? How do you like them, compared to other brands? What is this install for? Ross0 -
knights
Nice install very simple. We did our first wall hung night last month. I like the new set up and like that the air seperator for the heat exchanger is on top of the boiler outside the jacket.0 -
Very Nice
Thanks for sharing, once again. Your job pic's always give me something to work towards. Does your wiring include all of the EMT work and bringing power to the units? If so, is this normal for most of your installations? As a plumber, I am in the process of studying controls and basic wiring- just want to know how far I potentially have to go with it. Thanks again.0 -
Nice
Nice work with the Curvo. Fostapex looks nice too. What is your protocol with the fill valve? Do you fill and then turn it off? Is that a Caleffi brand that operates under line pressure until "equalizing" out at the pre-set or 12psi mark?
Another question...What kind of Delta t are you running? (at design conditions) 420,000 btus with 20ea 1/2" loops at a 20 degree Delta T = 2.1gpm per loop. Pump looks like a 15-58?
Inquiring minds want to know.
Paul0 -
That Rocks!!
Man oh man, I love the bends! Is it very common to bend the pipe rather than use fittings?
Also, all the manifolds I've done (probably 4 haha) are all with 1x1/2 tee's. How did you do your's?
aaand, after looking again, is there any reason that the expansion tank is teed in with the fill line instead of having it straight off the separator?? Is it to have fresh water going through the scoop before the rest of the system? Certainly not questioning your work, just very curious!!
Looks great
Thanks,
Rankin0 -
Thanks gentlemen
Jason on this job the electrical contractor did the wiring. I did the rubber cord to the circs on a weekend to get it running. The electrician may flex them if the inspector so desires. Gas pipe and water was done by the plumber. I left him room to add a backflow device.
The manifolds were built to order by Watts Radiant. Great quality, pressure tested and polished when they arrive. Saves a lot of time.
Location of the two Webstone valves assured a good flush and purge through the boilers, well worth the money.
I remote mounted the expansion tanks with FostaPex just to fit the space better. They wanted everything on one wall. As long as the expansion tank is located so the main circ is pumping way, actual location is not a concern.
The Caleffi fill valves are great, easy to adjust, nice built in shut off valve and spring check.
Paul the design is from Watts Radiant Works 253,396 load (the engineer had a copper tube 634,00 in the spec) Those are the new 26-99 3 speed circs in all 3 places. Hard to find a system pump with a 25 gpm flow at 6.10 ft of head! Nice pump, I really like the way the pump flange holds the nut, no need for two wrenches to tighten, nice feature. 400 foot loops of 5/8" RadiantPexl
This is the first time I have used a Honeywell purger in quite a while. It's what the supplier had on the shelf, I like the Caleffi normally. It worked great, they have made some nice improvements.
Yeah, Ain't it funny how the Knight moves?
Sweet job. Simple, yet all there...
TimJust a guy running some pipes.0 -
Leave your Signature
The long sweep bends tend to be your signature Hot Rod (and they make great sense) You must own a T-Drill or a similar tapping device. Gives you alot of flexability to customize.
Like the compact layout!
Rich0 -
exp. tank
What type strap is holding the expansion tank? I've noticed this method on your pics, looks very clean.0 -
the straps are
made for me by a local sheetmetal shop. I'm designing a better one that holds the tank upright, the prefered mounting position according to most installation manuals.
Although I don't know a sideways mount limits the life expectancy, for sure.
- 85.7K THE MAIN WALL
- 49 Biomass
- 72 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 39 Industry Classes
- 15 Recall Announcements
