relief valve

Dave_4
Member Posts: 1,404
Heating question for a standard atmospheric vented 50 gallon hot water heater that is being used for space heating? What should be used for the relief valve, A standard T & P valve or a #30 relief valve rated for hot water boiler? The present valve is now leaking due to a faulty fill valve. The valve that is on now is a #30 relief valve. What is the proper valve that should be on.
0
Comments
-
PRV
Since the unit UL is listed with the PRV it must stay on . But since your using it for heat add the 30# valve . Also you need a secondary high limit . We usually add it to the Thermal
couple There s a jumper made by Honeyweel that will work0 -
relief valve
Jim, Should this heater have both relief valves installed, the hwt&p and the #30 relief ??0