circulator for hot water zone

How many heating zones do you have? If each zone is driven by individual pumps (vs. zone valves), you will have independent relays controlling each pump.

Do you have a volt meter? Are you familiar with using one? This will tell you where the voltage ends; work backwards from the pump. If you don't have one and/or not familiar with using it, get some who knows how, i.e. a heating professional.

Comments

  • tom_103
    tom_103 Member Posts: 6
    circulator for hot water zone

    1 zone is not working,circulator doesnt go on how do i know if its needs to be replaced
  • tom_103
    tom_103 Member Posts: 6
    circulator for hot water zone

    1 zone is not working,circulator doesnt go on how do i know if its needs to be replaced
  • Check

    the power to the circulator. If there is none, work backwards; it could be the relay, thermostat, power source.....

    If the circulator is bad, it's usually too hot to touch. All that electrical energy turns the motor into a heater.
  • tom_103
    tom_103 Member Posts: 6
    circ cool

    if relay was bad wouldn't other zones not work. also therm for that zone operates air
  • Weezbo
    Weezbo Member Posts: 6,232
    that might be ....

    a frozen coil or three way motorized mixer in the F.A. unit.

    if the other zones open and close and the circ is running...then the problem is likely in the "field".

    man i type slow.

    the added information would have helped Alan divine a solution quicker*~/:)
  • tom_103
    tom_103 Member Posts: 6


    my boiler has 3 zones w/ taco 1/25 cont duty circs. 1 aquastat and a relay switch on burner
  • tom_103
    tom_103 Member Posts: 6


    sorry if i wasn t clear