Radiant Zone Valves
bob_46
Member Posts: 813
Unless you have an unusual situation like a super high head pump regular zone valves should work fine. I don't think you would need the strainers with regular zone valves as they are not as sensative to a little debris as those solenoids. bob
Watts Valves
Look at the pics below. The customer has 6 of these zone valves, each feeding a 3/8 radiant loop. I've never seen this set up before. I understand the valves, but why the check valves? And right after the checks is a 1/2" x 2" reducer with a 2" plug in it. Some of those are mounted upright and some are at a right angle. And how about that junction panel?
The customer wants to replace them. Any recommendations?0 -
Good golly, what a mess!
My thoughts go to either a Viega or Wirsbo/Uponor manifold, with telestats instead of the ancient zone valves....and a Taco ZVC control to simplify all the wiring.
Getting the tubing to pex won't be a big task, but ridding yourself of all those extra fittings and check valves will make things look so much nicer. MHO....Chris0 -
those old valves are older than Sam's Hill /\. *~/:)
the cobwebs and the no grounder should illuminate that idea
i have not seen them in decades:)
wow! Lol , rethink the whole strategy
Thanks Guys
Yeah, It really does make sense to cut it all out and start from scratch. I'll relay the info back to our sales guy.0 -
Hey Paul,
Do you think those reducer couplings right after the checks could be a "mini hammer arrestor"? That's all I could come up with...
Part B, may be to find out how big those zones/loops are...Are they too long for their own good? If memory serves me, (don't count on it!) even 3/8ths copper loops should be kept to under 275'...and should be as equal as possible, while the flow needs a pretty large pump.
In the picture, it looks like there is more going on from the main...than the little radiant zone/zones being shown. Could this also be a call for some type of mixing?
Just thinking out loud after viewing the photos again. Chris0 -
Thanks Chris!
You've brought up some very good points. The only radiant I ever put in was in my garage, and I've serviced very few. I don't recall seeing any kind of temperature control on this system.
And yeah, a hammer arrestor makes a lot of sense. I'm sure those zone valves just snap shut, unlike a honeywell 8043 type.
Think I need to take another look.0 -
I think
those are strainers not checks. I agree with the hammer arresters idea. I would ring out all the wiring and figure out what the original sequence of operation was. bobThere was an error rendering this rich post.
The supply house sent over cuts for new Watts valves. $300 + each. Couldn't this just be done with your basic honeywell valve? And use some sort of zone panel?
Chris, I found out there is a mixing valve on the system. Probably not the best way to regulate radiant temps, but there is something.0 -
OK, thanks Bob.0