Are hot water and steam radiators interchangable?

GatewayKBo
Member Posts: 1
We have purchased an old home that is missing many of its steam radiators. It is a one pipe steam system. There seems to be a shortage of used one pipe radiators on the used market in St.Louis MO area but plenty of used hot water and two pipe steam radiators. Can I use these for a one pipe system by plugging the extra hole and drilling and tapping in a vent port? Are there any other considerations?
0
Comments
-
Yes you can
just make sure you use the right size pipe connection to the radiator. This may mean you have to remove and replace a bushing, which can be difficult, but it's the right way.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0