Munchkin T80M combustion
Howdy folks - Glad I found this forum. I DIY'd a Munchkin T80M last spring. P/S setup with the DHW on the secondary along with 3 BB heating zones. Everything seems fine but I wanted to a few opinions on the combustion trim since I'd never set one before. What I currently have:
RPM CO2% COppm O2% Lambda Eff
120 9.5 15 4.2 25.1 88.2
530 9.1 76 4.7 29.8 88.2
Measurements using a UEI C75. Elevation is about 5,400 ft so the air is a bit thin to start with. I don't have gas pressure. Could use some guidance on building and hook-up of manometer.
Long story made short, I think the trim is ok since it's in HTP specified range. I can take the CO2 down to the lower end of HTP's range with about a quarter turn on the gas valve.
What do you folks think?0 -
CO2
Is this Natural gas or LP? If it's Natural, I think your CO2 in Hi fire should be higher than is low fire.
Also your CO in hi fire may be a bit low.
Adjustments to a gas valve should be done by a trained professional.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements