Vaporstat Purchase - Wiring Question
Tom Hopkins
Member Posts: 554
Question-
I would like to replace my pressuretrol with a vaporstat. I see 2 similiar 0-16oz models... one is the L408J1009 and the other is the L408J1025. The difference according to the manual is that the 1025 omits the "B" terminal and only has R and W, and it "makes RW" on pressure rise.
The 1009 has R/W/B terminals, and on pressure rise it breaks RB and makes RW. Is this the model that I want, and I should wire to it RB so when I hit the main limit it breaks?
Just want to make sure I order the correct model.
Thanks!
I would like to replace my pressuretrol with a vaporstat. I see 2 similiar 0-16oz models... one is the L408J1009 and the other is the L408J1025. The difference according to the manual is that the 1025 omits the "B" terminal and only has R and W, and it "makes RW" on pressure rise.
The 1009 has R/W/B terminals, and on pressure rise it breaks RB and makes RW. Is this the model that I want, and I should wire to it RB so when I hit the main limit it breaks?
Just want to make sure I order the correct model.
Thanks!
0
Comments
-
The 1009
is what you want. And you're right...R(ed) to B(lue) for BTU's...breaks on pressure rise.
Happy Steaming!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
What about this one?
model L408A1132?
0 -
That one will
work, too. It is the older mercury model.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements