Vaporstat
tom_11
Member Posts: 58
It is a one pipe system, gravity return. the longest run of 2 inch pipe is 18 ft . thank you tom
0
Comments
-
vaporstat
I have a weil mclain 368st oil fired boiler,n would i benfit in anyway by installing a vapor stat,insted of a pressuretrol? if so what be the setting for the vaporstat. thanks tom0 -
Yes
Not knowing your system extent or type, there are some variables. But even a reasonable one or two pipe steam system can operate at between 8 and 10 ounces cut-out pressure.
Think of your piping and steam carrying capacity at a certain pressure drop. Many old systems were designed for between 1 and 4 ounces pressure drop per 100 equivalent feet of pipe. If your longest run of piping is 50 feet with six elbows, you are probably at 100 equivalent feet or less, as a point of reference. That may take just four ounces, with the return being by gravity.
Two-Pipe systems can do even better because of the separate return path for the condensate."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements