Air pressure keeps dropping to zero
tim smith
tim smith Member Posts: 2,839
My guess is if you see no water on floor anywhere then you probably have an underground leak on a pipe? just a thought, scary as it may be. Tim
  • Jeff_107
    Jeff_107 Member Posts: 6
    Air Pressure keeps dropping to zero
    Hi - I have a loop hot water heating system and the pressure gauge which was stabilized at about 12 lbs has dropped to zero. I have to put water back into the system for the pressure to rise back to normal. (12psi)
    Any suggestions? leak in expansion tank? air in the lines.
    The auto fill line is open and working.
    Thank you
    Jeff
  • martin
    martin Member Posts: 144
    No Pressure
    You have a leak somewhere,If you put it in to go back to 0 it has to get out somewhere. I think your auto fill isn't working for that should keep it up to pres. How long does it take to depressuize and how often have you had to fill it.
  • Jeff_107
    Fill it every day
    I have to fill it every morning. I check the autofill and water seemed to be going into the system. Do you think the leak is in the expansion tank?
    Thank you
  • Leo
    Leo Member Posts: 770
    You may have a crack
    You may have a cracked boiler and the water is escaping as steam up the chimney. Couple this with a bad feeder as they do fail and you have zero pressure.
    Leo
  • Jeff_107
    I emptied the expansion tank and no water
    The expansion tank has no water in it - is it supposed to have some - even a little? I hope its not a underground pipe. How would you be able to tell. There is no water under the baseboards or near the bolier.
  • The ohhh ahhhh test define
    First off, this can ONLY be done with a high mass boiler. No copper fin tubed pr low mass stainless steel boilers.
    Disconnect the circulators electric line.
    Turn a thermostat up to fire the boiler and keep the make up water on and keep the boiler pressurized.
    As the water is heated and pressurized, it will flow towards the breached piping. CAREFULLY feel the supply and return pipng. You will be able to feel where the hot water is flowing to. If at all possible, isolate the return line with a valve so the water has to flow in a forward direction only. If it is a breaching in a copper line between baseboards, you should be able to feel (ooohhh) the water flowing from the heat source, to and through a section of baseboard. Eventually, you will find a place where the water flows into the ground, but doesn't come up at the next baseboard riser(AHAHHHhhhh!!).
    Now, if you don't have access to a non contact infrared thermometer, you tank take your shoes off and shuffle around in your stocking feet to find the hottest floor spot. (ahhhhhh) .
    Now its time to do some jack hammer surgery... Put your shoes back on first.
    G'Luck.
    ME
  • Jeff_107
    Auto fill
    I disconnected the cold water suplly line to the expansion tank. the water is on, however it doesn't fill it back up. Is it poosible the check valve in the expansion tank is the problem?
  • jp_2
    jp_2 Member Posts: 1,935
    what if you
    drained the system, fill with air and listen for the leaking air?