leaking Gortons....
I thought the Gortons had floats inside of them.
Dave Stroman, Denver
  • kpc_5
    kpc_5 Member Posts: 4
    anyone been..
    Having issues w/ Gorton main vents not shutting off and leaking/spitting water? I have had a couple of #1 and a #2 that have been leaking on 1 job...replaced then very soon after the call comes that they are having issues w/ water all over the floor....They are installed up on the dry return up and away 8" from the drop back down into the wet return boiler...ty,kpc
  • tim smith
    tim smith Member Posts: 2,886
    Regarding spitting vents
    Could it be the wet return is partly blocked and water backing up to vent?? just a thought. Tim
  • kpc_5
    it a good thought,....
    I have flushed out the bottom of the boiler a lot as of late...nasty stuff. It could be partially blocked.But there is only a very small part of the system that is wet. I will check...ty
  • kpc_7
    kpc_7 Member Posts: 9
    Bingo!
    pulled apart the returns this am...it was plugged on the vertical portion of the tee...what a mess. redid them in copper below the waterline. ty