DHW gravity recirculation
andy_21
Member Posts: 42
We are having a new heating system install as I type, Knight 105 w/ 80 gal Super Store Ultra.
On My old hot water heater instead of a pump on the recirculating line, there was a swing gate check valve w/ a 1/4" hole drilled into the gate, piped into a tee @ the bottom drain. This set up always a worked in having almost instant hot water @ the furthest fixture. On the new tank the cold inlet is @ the bottom. Can they still use the same piping set up as my old style tank or must it be pumped?
Also is there any time the condensate water should not be run thru a neutralizing set up, before pumped into sewer system.
Thanks
On My old hot water heater instead of a pump on the recirculating line, there was a swing gate check valve w/ a 1/4" hole drilled into the gate, piped into a tee @ the bottom drain. This set up always a worked in having almost instant hot water @ the furthest fixture. On the new tank the cold inlet is @ the bottom. Can they still use the same piping set up as my old style tank or must it be pumped?
Also is there any time the condensate water should not be run thru a neutralizing set up, before pumped into sewer system.
Thanks
0
Comments
-
Try first. A circulator can be added if needed. If so, look for the tiniest circulator you can find as the needed flow will be in gallons per hour not minutes.0 -
Recic.
This should work fine as long as you have slope, we have done it many times.
0 -
Thanks for the input, but I was wondering where they would hook the check valve to, the cold water intake, recirc intake?
Thanks0 -
The cold water intake will become the recirculation intake. I'd install a tee very near the intake. Use the branch for the fresh water then install the check valve a reasonable distance (say at least 4 pipe diameters) away from the tee. In other words, in this order: check valve, tee, tank.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements