steam (short cycles)
Dan_43
Member Posts: 57
I am in the basement doing paperwork and I hear my new Burnham IN7 boiler cycling off and on very often. The controller is set at about 1.5 lbs and the dif. is at about .75 lbs.
I just watched the cycle, the boiler shut off at about a half a pound. Do you think it's the Honeywell programmable thermostat up stairs that making the boiler turn on at a fraction of a degree drop and shut off at another fractional rise? the thermostat is on an interior wall.
Dan
I just watched the cycle, the boiler shut off at about a half a pound. Do you think it's the Honeywell programmable thermostat up stairs that making the boiler turn on at a fraction of a degree drop and shut off at another fractional rise? the thermostat is on an interior wall.
Dan
0
Comments
-
thermostat
did you configure the thermostat for steam? If a new thermostat is used "out of the box" then its still set up for forced air (the default factory setting) and will short cycle the boiler wasting energy.
-TerryTerry T
steam; proportioned minitube; trapless; jet pump return; vac vent. New Yorker CGS30C
0 -
It is 3 years old but I know I never did anything to it. How do I do make the ajustment?
Dan0 -
short cycle
Hi Dan, many times a steam boiler short cycles because of a clogged pigtail, which is the curved pipe that your pressuretrol is attached to.
Regards, Monty.0 -
This is a new installation, do you think it could clog that quickly? Also I have (2) pressure gages on the boiler and they are only on about 1/2 lbs when the boiler shuts off?
what do you think about the thermostat theory?
Dan0 -
burnham
Hi,
I have baseboard water heat. Heater uses gas and its model is burnham PXG-200AA-WNI, 82000 BTU gas water heater. I just replaces water in the entire system one month ago, now since last 15 days I see water vapour comming out of the heater setup. Is this a problem? How should I fix this? I just paid 250 so get the water out a month ago so do I have to call technician ?
Please help !0 -
Download installer instructions from Honeywell
Find the page at Honeywell for your tstat and download the installer instructions. If you have a VisionPro 8000, you would enter installer setup by pressing system, then holding down buttons 3 and 5 of the 7 along the bottom row, until the display changes to a 4 digit function code and a 2 digit setting code. Use the up arrow to change the function code to 0240 (first stage heat cycle rate) and make sure the setting code is 01, for 1 cycle per hour.
I recommend you find the setup instructions for your model online and go through the settings one by one to make sure they all make sense.
0 -
thanks I will contact Honeywell tomorrow for the information If I have to buy a new one for the options than so be it.
Dan0 -
Dan, Did changing the settings help with the frequent cycling of your boiler?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements