one radiator not getting water flow

Mike T., Swampeast MO
Member Posts: 6,928
Assuming you can access the <I>plain</I> return tee, I would replace with a monoflow tee--just remember that they're installed in the opposite direction those serving the supply. If you're lucky that added resistance will force sufficient flow through the rad--otherwise things can get messy, complicated and expensive...
0
Comments
-
one radiator not getting water flow
Got a mono flo system 2 zones and one upstairs room is not getting heat/flo. Its 1 1/4 main line with 3/4 monoflo feed just a reg 1 1/4 X 3/4 tee on return. This room upstairs has the feed and return seperated by about 7'. I have no idea how the pipes are run thru the walls and why the space between the pipes, which i think is part of the problem. I was thinking i might install a valve to shut off the flow to the rest of the system and force the air up and out and start the flow. Any other ideas or might this work. Thanks0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements