Sight Glass level at bottom, no LWCO?
GW
Member Posts: 4,832
you must confirm with draining water out, if things are gooked up you'll be thrown a curve call.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=368&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=368&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Hello! What is happening when the sight glass water level is at the bottom, and the LWCO is not turning off the boiler? I know the LWCO works, and I know there is plenty of water in the system, but I'm seeing something weird here...any ideas?
Steve0 -
Sight Glass
The pet cocks on the gauge glass assembly could be plugged or shut off. Could be the top or bottom .There was an error rendering this rich post.