Looked into a side arm convertor off the side of the boiler? Or go into Dan's Resource (library) and look up "System Piping Techniques" there is a well written article there about taking a hot water zone off of a steam boiler.

Good Luck!

Comments

  • Bill_99
    Bill_99 Member Posts: 2
    Can I use the tankless coil on my steam boiler to heat a room

    I have a room that needs to be heated, but I have been told adding to the steam system is impractical. Can I attach a circulator and expansion tank to the tankless coil and heat the room with the hot water? My other options are quite costly!
  • Ken_40
    Ken_40 Member Posts: 1,310
    Absolutely yes!

    Done it many times. Piece of cake.

    Use the coil to heat anything (radiant, domestic hot water or simple HWBB - OR ALL AT THE SAME TIME!

    Easy to do. Simply think of the hottest demand water temp required. Pipe the inlet and outlet as a bypass arrangement. By placing a small ball valve between the in and outlets, you can control how much bypasses the coil and how much passes thru. Remember the coil is a source of BTU's - not the pathway per se.

    If you need a sketch/schematic, let me know.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Ken's right

    We do it every once in a while . A few things to consider .... Has the coil been used for hot water ? For how long ? I'd try to clean the inner part of the coil if it was used a long time .

    And you can only heat so much extra space before it'll stop the boiler from steaming . I believe , if the boiler is sized right for your home , you can add 33 percent extra in btus of the boiler you have . To get around that if you have problems you can always prioritize the steam zone .

    Here's a recent install where we used the coil for a baseboard zone . There was no need for a bypass - with the boiler steaming , the highest temp to leave the coil was 190 .