Snowmelt
Bob Forand
Member Posts: 305
Hello all, I am involved with a snowmelt project that has a Taco flat plate HX and a condensing boiler. The HX was sized for the load at high temp on the HX. Should there be a mixing valve on the snowmelt side of the HX. What
controls the temperature out in the slab ? Will modulation of the boiler vary that temperature so that there are high temperature swings going to the slab ? It is a Baxi HT165 with a Tekmar 665 control, that has the snowmelt/precip socket and sensor. There is also a zone of inslab that is heating the garage. That zone has a mixing valve on it.
controls the temperature out in the slab ? Will modulation of the boiler vary that temperature so that there are high temperature swings going to the slab ? It is a Baxi HT165 with a Tekmar 665 control, that has the snowmelt/precip socket and sensor. There is also a zone of inslab that is heating the garage. That zone has a mixing valve on it.
0
Comments
-
Why the heat exchanger?
that boiler could hook direct to the snowmelt, I'd use a hydro-separator.
Then you take the HX, cost, pressure drop, efficiency, and dual expansion tanks, relief valves, etc out of the price. Set the boiler for the design supply and let the tekmar turn it on.
I have Ultras, Contenders, Prestiges, and Munchkins all on various snowmelts.
I would suggest a good multi metal anti freeze. Rhomar Rho Guard or Nobel.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Snow melt
That tekmar control will ajust everything for you when set up correctly0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements