I am trying to find some good vibration-absorbing bracket for mounting a 75lbs circulator on 1 1/2 inch horizontal pipes. Any good recommendations? The mechanical room is in the basement of a church and the sound vibration has to be cut down to a minimum.
Luc
Luc
0
Comments
-
Any 75 lb pump...
should be vibration free before using it at all!
A vibration free circulator/pump is a good pump. Any pump that produces audible vibrations is a bad pump.
Fix the pump, don't move on - looking for vibration dampening.
The classic "noise" comes from pump damage at the cradle mounts. Sagging cradle mounts result in mis-alignment of the spring coupler and going through spring couplers from the imbalance like there's no tomorrow.
Spring couplers should last years, not months. Last note: Don't hang any part of the circ. pump; rather, hang the PIPE that goes into it's supply and return sides. The hanger of choice? Either a clevis hanger or a split ring hanger. The SR hanger can be inverted and floor mounted. Of course, there's a little more to it than that, but good ole common sense will prevail - I'm sure.
There are spring-like "absorbers" that can be inserted where the threaded rod comes form the ceiling, if you insert a connecting "joint." I would urge you to fix the vibration source, not allow it to continue - and mask it.
Let us know how you make out.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 103 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 936 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements