Radiator Question

amhplumb_2
Member Posts: 62
Belated thanks Brad, started to the same day and called away from the screen, in my mind I did it, crazy month! The job is working out well. Doing it sections at a time off of new header using 1-1/4 (vs the 2-1/2"!) and P/S pumping. The customer was amazed seeing 3/4" replacing 1-1/2 to one of the rads! Good ol' gravity sizing! The TRV on the huge rad in the living room eliminated temp swings in the room!
Al
Al
0
Comments
-
Radiator sizing question
Fellow Wallies, what factor do you use for equivalent foot/feet, for radiators when calculating head loss in sizing the circulator & the piping? My IBR tables only have for baseboard, and I have never sized for rads before! Are there tables, a formula, or a rule of thumb? I have a project where I am replacing a boiler and re-piping an old gravity converion system in which the piping is now way oversized. Fortunately my customer wants to keep the rads! My heat loss calculations show the rad's to be right in the ballpark all over a bit! Thanks!0 -
Pressure Drop of Old Cast Iron Radiators
Negligible. Think of 1.0 GPM flowing in a 3/4" pipe. Head loss somewhere above Paris Hilton's dog's IQ. Easy to deal with.
I mean the head loss.
Take that same flow. Think about is as being put it into a large room at very low velocity... even with a TRV, assuming 0.25 feet of head is pretty conservative.
Bottom line: If you are using a TRV and know the flow rate (you should do both IMHO), then take the TRV delta-P and add ten percent to it. Sleep well.
If your radiator to heat loss ratio is high (as it nicely so often is), you are doing a service to the Owner. Outdoor reset and old cast iron is a marriage of love."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements