Wiring change on Taco relay and triple aquastat ?

Joe Mattiello
Member Posts: 735
Thank you, for bringing this topic up. The change in wiring is to prevent the boiler from firing when the boiler is shutoff using a safety switch. If the ZR/ZR terminals are connected, and the switching relay is using another power source not connected to the safety switch the burner could still fire. For your reference I attached the published safety notice.
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions
0
Comments
-
I think this started a few months ago ?
When integrating a triple aquastat with a Taco multizone relay , it used to be as simple as connecting a wire from ZR to ZR and ZC to ZC .
Now you have to run ZR of the aquastat to X of the relay , and ZC of the aquastat to the other X of the relay , with a jumper to ZR .
Why the change in wiring ?0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 103 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 936 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements