If the boiler can run a high enough ΔT, perhaps try to heat the water in 2 steps?
The final heat exchanger would get the hot boiler supply water first and then its return (which would be above condensing temps) would be be the supply for the secondary heat exchanger which does the first stage of DHW production (preheat the DWH to a certain level).
With a boiler that can handle a ΔT of 30 to 40° you could possibly use a 160° supply along with a final 120 - 130° return, while making 140° DHW in the second stage.
The final heat exchanger would get the hot boiler supply water first and then its return (which would be above condensing temps) would be be the supply for the secondary heat exchanger which does the first stage of DHW production (preheat the DWH to a certain level).
With a boiler that can handle a ΔT of 30 to 40° you could possibly use a 160° supply along with a final 120 - 130° return, while making 140° DHW in the second stage.
0
Comments
-
high efficiency for DHW production
Hello all,
Has anyone used a high eff boiler solely for DHW production through a heat exchanger?? Will I ever condense??
Regards,
Josh W0 -
yes to both -
> Hello all,
>
> Has anyone used a high eff boiler
> solely for DHW production through a heat
> exchanger?? Will I ever
> condense??
>
> Regards,
>
> Josh W
It depends on your expected DHW temps. Very hi temp DHW (and then mixed down) offers some challenges but normal DHW production temps (115 - 120) will condense.0 -
yes to both -
It depends on your expected DHW temps. Very hi temp DHW (and then mixed down) offers some challenges but normal DHW production temps (115 - 120) will condense.0 -
Sure
I have seen it done, especially where the water quality is sketchy.
You would want to use a good indirect, capable of giving you a high Delta T.
Supply that with 160 degree water; that would put your return water at 130 to 135 ish, making the boiler condense.
Remember, in doing this, you will be "firing" the indirect below it's recommended rate, so you may have to compensate by going up a size in volume ( without going too much over the rating of the boiler)0 -
or...
use a high quality tank like trangle-tube's series, etc. to provide you with a very large HX surface that requires a very low supply temperature, maximizing your chances to have the boiler condensing all the time.0 -
a dual coil indirect tank
is my current method. I use the Heat-Flo tanks with two 1-1/8" coils. Lots of coil or surface area and lowest possible return temperatures to the boiler will be the ticket.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements