How Do I Purge my Hydronic Heating System?????
Joey
Member Posts: 3
I have a gas furnace and 2 zones for hydronic heat. I can hear a little gurgling in the pipes and I'm sure there is air somewhere in the system. Question is: How exactly do I purge each zone? Click the link below or copy and paste it for a sketch of my system, that might make describing easier. Basically, in order to purge each zone, which valves do I need to shut off and which stay on.
http://i120.photobucket.com/albums/o199/jfon0604/Furnace.jpg
How long do I run the water through the system? After its all said and done, what pressure should I put the system back up to.
Sorry for all the questions, I appreciate any help!
Thanks.
http://i120.photobucket.com/albums/o199/jfon0604/Furnace.jpg
How long do I run the water through the system? After its all said and done, what pressure should I put the system back up to.
Sorry for all the questions, I appreciate any help!
Thanks.
0
Comments
-
purge system
Your system was installed with future service in mind. Lots of isolation valves are good!!
For zone 1>
1.Close valve 5
2.Open valve 1
3.use the quick fill on the feed valve #1.
4.Watch the pressure guage. Keep between 15-20 lbs.
5.Continue until air stops coming out of the hose.
6.Close quick fill, close valve 1 make sure pressure is between 10-12lbs. if not bleed off more water through valve 1.
7.Open valve 5 and your done.
Repeat for zone 2.
using valves 4 and 2.
Good luck.0 -
simple...
-1- shut boiler
-2- shut valves 4 and 5,
-3- hook up a hose to bib above #4
-4- if your boiler's water feed pressure regulator has a lever, lift it straight up to pressurize the system but keep it below 25psi or the boiler's pressure relief valve will open - you might need to play with this lever up and down as you purge, remember the original pressure - the correct pressure cold is the highest point in the system - minus the lowest point in the system in ft divided by 2.33 + 5 - that should be your cold static pressure - eg if you system is 18ft tall, typical 2 story house - from boiler in basement to radiators at floor of level 2, then , 18ft / 2.33 = 7.7, + 5 = 12.7. 12.5 just happens to be the factory setting for most feed regulators, as well as the air pre-charge pressure, on expansion tanks
- the 2.33ft is because every 28inches of height is 1 lb of pressure, the +5 is to keep at least 5psi of pressure at the highest point to keep the pump from sucking in air
-5- open bib above #4 and drain on until water runs clear and quiet
-6- close bib and repeat for bib above #5
-7- drop feed bypass lever and drain any bib to bring pressure down to orginal level
-8- reopen valves 4 and 5
-9- restart boiler and have a nice day
For more detailed info you will have to buy dan holohans books and really learn about the systems0 -
Thanks so much your you help guys!! Quick question...does it matter if I shut both valves 4 and 5 at the same time to drain either zone? Or should I shut 5 and open bib 1, let it drain. Then open 5 shut bib 1. And lastly, shut 4 and open bib 2?0 -
You can shut them both together. Remember you are not draining the system you are replacing the existing water and (air) with new water via the feed valve.0 -
Great!! Thanks so much for your help!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements